2009 fpso research forum dsme
TRANSCRIPT
-
8/13/2019 2009 FPSO Research Forum DSME
1/18
000045
1
Safety Concept of DSME LNG FPSO:A shipbuilders perspective
Sung Hoon Sean Kim, Ph. D.
Daewoo Shipbuilding & Marine Engineering
April 12009
2009. 4.12Future Products & Business Development Institute
-
8/13/2019 2009 FPSO Research Forum DSME
2/18
000045
2
2009. 4.13Future Products & Business Development Institute
Recent/On-going projects
2009. 4.14Future Products & Business Development Institute
TOC
DSME HSE Engineering
Risk on Offshore LNG Plants
Comparison with those on Oil FPSOs
DSME LNG FPSO Features
Layout
Process
Safety Devices
-
8/13/2019 2009 FPSO Research Forum DSME
3/18
000045
3
2009. 4.15Future Products & Business Development Institute
HSE Engineering in DSME
Drilling rig & drillships FPSOs
FSRU & LNG RV
Cruiseship
Reliability
2009. 4.16Future Products & Business Development Institute
LNG RV
Reviewed by LRNA & ABS
FERA
Regas facilities besidestrunk deck of No. 1 tank
Jet fire
Fire rated walls toprotect tanks
SUS Plating & Deluge atthe pump bottom
CFD Explosion analysis
Leak in the STL
Effect of Relief panel
Ventilation condition
FRA, reproduced byDSME using Neptune
-
8/13/2019 2009 FPSO Research Forum DSME
4/18
000045
4
2009. 4.17Future Products & Business Development Institute
LNG FSRU
A research project FRA using Neptune Emergency relief design
Vent Flare
Toxic gas dispersion Collision Risk Assessment
2009. 4.18Future Products & Business Development Institute
Risk on Offshore LNG Plant, Myths & Facts
Myth
Explosion comparable tohydrogen bomb
Collision or vulnerability toterrorist attack?
Spill on water
Rapid phase transition (RPT)blast?
Vapor cloud traveling towarda center of population?
Total collapse of containmenttank?
A pool fire within the full tankimpounding area?
Tank top fire?
Fact
Embrittlement of steelstructure exposed to cryogenicspill
Dangerous process
High pressure, flammable
and/or cryogenic fluid Flammable refrigerant maybe
Safety by distance shall be
compromised
-
8/13/2019 2009 FPSO Research Forum DSME
5/18
000045
5
2009. 4.19Future Products & Business Development Institute
Inherent Safety LR Guidance
Adequate separation / segregation of hydrocarbon inventories
Reducing the level of confinement in a hazardous area
Minimising the size of hydrocarbon inventories available for escalation
Suitable location or protection of essential systems and equipment
Use of passive systems, i.e. fire and/or blast walls and PFP, includingprotection against spills
Use of active protection systems, i.e. fire fighting, ESD, PSD.
2009. 4.110Future Products & Business Development Institute
Approach to Assess the Risk
Independent studies
Leak frequency
Dispersion
Flammable gas evaporated from LNG release Offsite hazard impact irrelevant on an offshore plant
LQ impairment due to exhaust or flammable gas, smoke, etc
Fire
Jet/Pool fire & the frequency of escalation
Passive fire specification
CFD Explosion
Congested semi-closed modules
Ductility level blast specification
Drop object
Collision
Side-by-side offloading and/or tandem offloading
QRA
Not only related with the process failure but with non-hydrocarbonaccidents
-
8/13/2019 2009 FPSO Research Forum DSME
6/18
000045
6
2009. 4.111Future Products & Business Development Institute
Oil FPSOs by DSME
Pazflor
AGBAMI
2009. 4.112Future Products & Business Development Institute
Comparison of Risks on Oil FPSO & FLNG(1/2)
- Liquid inventory rather limited
- Liquid spill to be driven overboard- To be evaporated with energy fromambient air
- Large liquid inventory along the
process- Spill containment over the deck
-Heavy hydrocarbons with smoke
- Little evaporation when released
Pool fire
-Dense vapor just release from LNGprocess would slump over the deck
- Less confined and congested topsideto have better ventilation
- Little smoke
- Process gas heavier than air
- Smoke from the pool fire shall be
considered
Dispersion
- Readily dispersed and having lessreactivity
- Large explosion reactivityVCE
- High pressure gas inventory wouldhave more risk of jet fire
- Larger heat radiation
- High pressure gas at compressormodule
Jet fire
- Mainly C1- Hydrocarbons mainly heavier thanC3, C8, C10 and a little C1
Composition
FLNGOil FPSO
-
8/13/2019 2009 FPSO Research Forum DSME
7/18
000045
7
2009. 4.113Future Products & Business Development Institute
Comparison of Risks on Oil FPSO & FLNG(2/2)
-Mainly risers through internal turretcontaining mainly gas
- Enclosed space to be mechanicallyventilated
- Two phase feed liquid
- Mainly exposed riser inlets at one
side of the vessel containing mainlyliquid
Well fluidreception
- Hot wet flaring
- Cold dry flaring
- Cold vent
- Hot wet flaring
- Cold dry flaring
- Cold vent
Flare & vent
Side-by-side & tandem offloadingTandem offloadingOffloading
- Welded stainless piping & equipmentwith the minimum number of flangeconnections
- Deluge to prevent brittle fracture
- Vapor cloud control
Cryogenichazard
Ex. 1, Large scale FLNG, 460x75 lifting50,000 ton topside ~ 1.45 ton/m2
Ex. 2, DSME LNG FPSO(Mid size),330x65 lifting 20,000 ~ 0.93 ton/m2
Ex. Agbami, 320x59 lifting 35,000ton topside ~ 1.85 ton/m2
Plantcongestion
2009. 4.114Future Products & Business Development Institute
DSME LNG FPSO
330m x 65m, topside weight about 20,000 tonProduction 2 MTA through 2 trainsProcess deck 6m above the hull deck
Living Quarter located upwindFlare tower slantedGas turbines located above the process deckExtended anchoring platform
-
8/13/2019 2009 FPSO Research Forum DSME
8/18
000045
8
2009. 4.115Future Products & Business Development Institute
DSME LNG FPSO
Barge type hull Two rows of storage tanks
-Little risk from sloshing-Strong support for topside structures
Storage of 200K LNG/20K LPG Condensate to be consumed as fuel Internal turret system with weathervaning capability 2x5MW Azimuth thrusters
2009. 4.116Future Products & Business Development Institute
DSMEs Two-Row Tank/Design Evolution
Low sloshing load Small tank width leads to less internal flow
Avoid resonance with ship motion
No concerns on CCS against sloshing load
Strong support for offshore topside module Strong longi. bulkhead supports heavy
topside
Free from additional support for topside
Small deck deflection
Economical solution Cost-effective and optimum solution
comparing other Independent CCS
Centerline bhd. for
2-Row arrangement
138K LNGC 2-row FLNG
1080 1082 1084 1086 1088 1090 1092 1094 1096 1098 1100
Time [sec]
P
ressure
ImpactPressure TimeHistory
1RowTank
2RowTank
1-row
2-row
Experimental setup Model test
Pressure
-
8/13/2019 2009 FPSO Research Forum DSME
9/18
000045
9
2009. 4.117Future Products & Business Development Institute
DSME LNG FPSO
Conceptual development A competitive medium-scale model for offshore non-associated gas
well (less acid & lean) Liquefaction process
SMR technology of B&V, a renowned liquefaction technology
Client-preferring technology applicable
Gas turbine driven compressors to require smaller electric load
DSME design to Float, Storage, & Offloading A barge with internal turret system and facilities for side-by-side offloading
Gas treatment & utility modules design
Cargo handling system
Two-row arrangement of GTT NO. 96 CCS
Safety consideration Conceptual layout review in the current stage
Major FLNG safety issues being considered
Detailed safety study planned
2009. 4.118Future Products & Business Development Institute
Layout Living quarter
Separated from the process area
Protected by the Fire/Blast wall No jet fire grade
Ductility level blast design
To protect the lifeboat station
STL Compartment to be separated fromthe LQ via the lay-down area Blast attenuation
Safety against the jet fire & dispersion
Grated process deck to be extended tothe LQ for easy material handling &working path
-
8/13/2019 2009 FPSO Research Forum DSME
10/18
000045
10
2009. 4.119Future Products & Business Development Institute
Layout Internal turret
Harsh sea condition to prefer the internalturret system HP feed gas to be contained only within
the turret
Location To be located as close to the bow
For good weathervaning capability
Not to be close to LQ Blast relief Flammable gas Machinery space in the hull to separate
Structural integrity
Longitudinal deformation Swivel movement Blast loading
Mechanical ventilation No passive fire fighting on equipment &
structure inside the structure
2009. 4.120Future Products & Business Development Institute
Layout Gap for enhanced ventilation
Process deck Plated within process modules
To prevent the release from the topside to slump down to the hull deck
6m above the hull deck
Grated between modules to release flammable gas and explosion
Small safety gaps between modules to enhance ventilation Effect be analysed through CFD analysis
-
8/13/2019 2009 FPSO Research Forum DSME
11/18
000045
11
2009. 4.121Future Products & Business Development Institute
Fire risk
Jet fire Safety gap to prevent an escalation
from the jet fire
7 or 10 minutes of direct exposure
Dimensioning jet fire shall beidentified of the frequency of 1.0E-4/yr.
Deluge, ineffective to mitigate thejet fire
Heat up analysis
Pool fire For in-site layout, BS EN 1473
15 kW/m2 on the unprotectedmetal outer surface of anadjacent LNG tank
Design spill
For an FLNG,
Cargo tank protected within the
hull
Design spill from equipmentwould be limited
0.0950.0950.0950.08hc
0.70.550.40.25f
350300250180Totalheat flux
6540155Length
>30101.00.1
Lowesmith (2007) Gas jet fire
2009. 4.122Future Products & Business Development Institute
Layout Escape route
The primary on the hull deck
An alternative & material handling way on the process deck
The secondary crossway between modules
Full redundancy allowing impairment of one route
Port & Starboard
The secondary muster area (SMA) aft
Protection of SMA against fire, explosion and heat from the flare
-
8/13/2019 2009 FPSO Research Forum DSME
12/18
000045
12
2009. 4.123Future Products & Business Development Institute
Layout Clearance btn the hull & the process decks
Spaces for CCS maintenance Maintenance through liquid & gas dome
Retractable main cargo pumps
Favorable ventilation condition on the hull deck
Release at the hull deck
Hull deck piping of an LNG FPSO will be coarser than that of an OilFPSO.
Welded & insulated piping design of an LNG FPSO will be lesssusceptible to leakage.
2009. 4.124Future Products & Business Development Institute
Layout Topside Pipe Rack
Running above the main material handling way
Safe from material handling over the process deck
The material handling way as a ventilation alley & an alternativeescape route
Ladders between longitudinal modules
-
8/13/2019 2009 FPSO Research Forum DSME
13/18
000045
13
2009. 4.125Future Products & Business Development Institute
Explosion Risk
Release Dispersion Ignition Explosion Release frequency & inventory to depend on detail design
Dispersion depend on Ventilation condition : Layout, confinement, congestion, buoyancy,
Ignition source shall be rated
Explosion strength
Light hydrocarbon would have small explosion efficiency
Controlled by layout
Design Overpressure once in 10,000 years
Materials NG
Cold natural gas
Propane
Refrigerant
2009. 4.126Future Products & Business Development Institute
Layout Mixed Refrigerant & Storage
Mixed refrigerant Another source of flammable gas leak
C1, C2, C3, C5 & N2 Separate storage for C2, C3, & C5
Normally No Flow from the refrigerant storage to suction drum
Located at a well ventilated area
Away from LQ & SMA
Considering re-arrange vessels longitudinally
Hazard to be considered
Heat from the flare
Drop accident from crane
operation
-
8/13/2019 2009 FPSO Research Forum DSME
14/18
000045
14
2009. 4.127Future Products & Business Development Institute
Layout Offloading platform
Side-by-side offloading ofLNG only!
Protection
SUS plated under the gratedmanifold deck
Water deluges
QCDC & ESD
Consequence of release
RPT on contact with the waterwithin the gap would exert norisk
Explosion on the FLNG with littleimpact on the LNGC
2009. 4.128Future Products & Business Development Institute
Layout Flare tower
Tower slanted aft
With no condensate to be offloaded, no riskon tandem-offloading vessels
Flaring scenario (draft) No flaring in normal condition
Normal BOG will be consumed as fuel for G/T
Operation/Emergency flaring
Start-up Process shutdown
Separate vents for topside & cargo
Topside equipment maintenance
Tank purging
Tank pressure relief
Tip design & tower height will be determined
Heat shield on SMA
Heat on the MR storage tank
-
8/13/2019 2009 FPSO Research Forum DSME
15/18
000045
15
2009. 4.129Future Products & Business Development Institute
Typical Liquefaction Process
Liquefaction
CryogenicRefrigeration
System
Fractionation
Produced
WaterTreatment
LNG Product
Refrigerant
DehydrationAcid Gas
RemovalEnd Flash
BOG/FG
Compression
LNGStorage Tank
Flash Gas
BOG
CO2, Sulfur
H20
H20Condensate
Storage Tank
LPGStorage Tank
InletSeparation
C5+
C5+C3+C4
C1+C2
Fuel
FeedStock
2009. 4.130Future Products & Business Development Institute
SMR Black &Veatch, PRICO
Benefits of SMR Competitive efficiency Small equipment count Compact heat exchanger adopting
aluminum plate fin
A small number of drivers Limited inventory of refrigerant Simple operation
FLNG, August, 2007
-
8/13/2019 2009 FPSO Research Forum DSME
16/18
000045
16
2009. 4.131Future Products & Business Development Institute
Gas Treatment
AGRU
Little CO2 content in the feed gas from non-associated gas well
Dehydrator
2x100% Fractionation
Adjust LNG HHV & Stabilize condensate
Located around the midship to minimize the motion
2009. 4.132Future Products & Business Development Institute
Utility Gas Turbine
Gas turbine For MR compressor
Located at the upper deck above theMR process
Two trains configuration
Well separated from LQ
For electric power generation
Right behind of the LQ at the portside
Safe equipment requiring no hazardarea classification
Turbine blade rotor failure as apotential risk
Rather a common practice onoffshore plant
-
8/13/2019 2009 FPSO Research Forum DSME
17/18
000045
17
2009. 4.133Future Products & Business Development Institute
Safety Device Cryogenic spill
Piping of cryogenic flow over thedeck minimized
Around the cold box and the shortdirect run-down LNG piping to cargotank
Protection Shield for HP flanges
Drip trays for LP flanges
Local SUS plating may beconsidered
Management
Deluge under the offloading station Spill overboard
Evaporation by natural ventilation
Closed drain system to return largespill
Air blower away from the vessel
2009. 4.134Future Products & Business Development Institute
Safety Device Fire fighting
Passive fire protection - Fire rating
Design fire scenario
Jet fire rating
Large inventory hydrocarbon vessels including MR storage
Primary structure such as module stools, columns, base of the flare tower
SMA aft
Hydrocarbon fire rating
Fire wall behind the LQ
Active Fire Fighting
Water deluge on area & equipment
Dry powder system
Foam monitor
Details to be considered after FERA
-
8/13/2019 2009 FPSO Research Forum DSME
18/18
000045
2009. 4.135Future Products & Business Development Institute
Conclusion
DSME, prepared for HSE issues on an LNG FPSO!
DSME LNG FPSO Optimum design & layout will be developed to obtain
inherent safety
Process risk as well those from SMR will be controlled A compact process technology would enable a safer design
FERA will be used to manage the process risk!
Non-process risk will be controlled
HSE will be an independent discipline during wholeprocess of development
Systematic risk assessment
Structural design to withstand design accidental loads
2009. 4.136Future Products & Business Development Institute
DSMEFuture Products & Business Research Institute
Sung Hoon Sean KimT. +82-2-2129-0864
Thank you!