Continuous Cast Coolant Filtration and
Caster Water Filtration
Presented By Tom Horn and Mohammed Al-Bedour
Filtertech, Inc. USA
Global Continuous Casting ForumAtlanta GA. April 2015
• Filtration system concepts• Coolant temperature management• Different filter types
Important Filtration Questions
• Flow rate? (for entire system sizing)• Pressure required? (for pump sizing)
• Heat to be removed? (heat exchange)• Available cooling water? (cooling tower)• Type of coolant to be used? • Single or split mill coolant systems?
System Sizing Factors
• Filter size in gpm/sq ft (roughing/finish)
• Tank volume (20 min. ideal 10 minimum)
• Pump size and type
Gravity Flow to the Filter
Heat Exchanger
Clean Supply PumpRecirculation Section
Clean Compartment
Recirculation Pump
Filter
Rod Mill
Gravity Flow Into Flatbed Air Vacuum Filter 20 MT/Hr SCR Mill With CLI Feature and Re-Circulated Filtration
Drain by Gravity to Self-Cleaning Conveyor Tank, Pump to Filter
Heat Exchanger
Filter Feed PumpClean Supply Pump
Filter
Rod Mill
Conveyorized Tank
1000 GPM (3800 LPM) System with Conveyor Tank & Flat Bed Vacuum Filters
Split System Concept for Roughing & Finishing Mills
Finishing Mill
Heat Exchanger Filter
Clean Supply Pump
Re-circulationFeed Pump
Reservoir Tank
Roughing Mill
Clean Supply Pump
Filter
Conveyorized Tank
Heat Exchanger
Filter Feed Pump
Flatbed Air Vacuum Filters For Roughing Mill 50 MT/Hr
Flatbed Air Vacuum Filter For Finish Stands 50 MT/HR
Coolant Filtration for Continuous Cast Aluminum Rod
• Concepts and Components (Same as copper)• Air Vacuum with Lower GPM/ft² (LPM/m²)
allows more filter area for the application• Higher Coolant Concentration• Higher Operating Temperature
Coolant Temperature Management
Coolant temperature management includes both system heat removal and heat addition to enhance coolant and rolling mill performance.
Process Heat Removal
Temperature Sensor
Controller105 F
To Process
Clean Supply Pump
Cooling Water
In
Out
Heat Exchanger
Plate and frame heat exchangers precisely remove the process heat from the coolant controlling the temperature with cooling water
System Tank
Electric Immersion
Heater
Temperature
Sensor
Heat Addition
Temperature controller
85 F
Includes a tank heater or heaters that keeps the coolant warm during process down times to avoid cold production start-up .
System Tank
New Heating Loop System Design
Temperature Sensor
Controller
90 F
To Process
Clean Supply Pump
Cooling Water
Natural GasHeater
Heat Exchanger
Coolant Circulation Pump
Hot Water Pump
Hot WaterLoop90 F
Optimal Start-up Temperature
Heat removal Heat addition
Heating Loop Detail
System Tank
Temperature Sensor
Temperature Controller
90 F
Natural GasHeater (Boiler)
Coolant Circulation Pump
Hot Water Pump
TI PI
TI PI TI PI
TI PI
PI
Pressure ReliefValve
Condensateto drain
Expansion Tank Make-Up Water Inlet
Factors In Sizing
• Warm-up time• Tank volume• Required btu’s• Hot water flow rate• Coolant flow rate
Completed Skid
Benefits to Temperature Management with Heating Loop Design
• Significant Reduction of large “cobbles”• Improved tank temperature distribution• No hot spots due to heater contact • Lower energy cost by maintaining warm• Higher production rates due to less down-time • Extended coolant life with consistent
temperatures
• Flatbed Air Vacuum Filter
Filter Types
• Liquid Vacuum Filter • Deep Bed Gravity Filter• Band Filter
Air Vacuum and Liquid Vacuum Comparison
VS
Dirty Inlet HeaderOverflow Weirs
Air Vacuum Producer
Disposable Filter Media
Media Drive
End of Media SwitchVacuum Chamber
Clean OutletCarrier Belt
Spent Media Re-winder/Sludge Separator
Tramp Oil Skimming Trough
Air Vacuum Filter
•High differential pressure is developed below the liquid pool by the vacuum producer, and is independent of process.
Liquid Vacuum Filter
Clean Supply Pump
Filter Media
Spent MediaDirty Compartment
Vacuum Chamber
Pneumatic Vacuum Break
Clean Compartment
Dirty Inlet
• The vacuum pressure is created by the pump suction and filtration is dependent on the pump
Unique Design Features
• Efficient side seals• Controlled Level lndexing feature ( CLI )
Air Vacuum Filter Side Seal DesignStainless Seal Spring
Teflon® Stationary Seal
Moving Seal
Filter MediaFlatwire Belt
Belt Support Roller
Coolant Pool
Positive Side Seals (No Migration)
Controlled Level Indexing (CLI)
• The consistent vacuum produces a uniform pressure drop across the filter media.
• And a highly efficient filter cake removes more fines that means cleaner coolant.
Solids migration is minimized as the media very slowly enters the filter
Constant Coolant Level is produced
• The consistent vacuum also means lower power consumption. • Media usage will decrease due to efficient and uniform cake
Controlled Level Indexing (CLI)
Liquid Vacuum Filter
Clean Supply Pump
Filter Media
Spent MediaDirty Compartment
Vacuum Chamber
Pneumatic Vacuum Break
Clean Compartment
Dirty Inlet
• No positive side seals
• Long index cycle of media causes solids migration
A Liquid vacuum filter has no side sealing and the discharge is very wet copper oxides
Flat Bed Air Vacuum Filter with Media Re-winder and Separator
Gravity Filters
• Band Filters• Deep bed filters• Gravity with vacuum drying
option
Band Filter
No seals and no pool depth resulting in poor filter cake production
Band Filter
Light duty construction does not meet mill high standards
GSF Gravity Filter
Deep Bed Gravity Filter With Extended Ramp & Drying
Filter Media
Flat Wire Belt Conveyor
Dirty Inlet Header
Optional Sludge Dewatering & Drying UnitExtended Drying Ramp
Clean OutletDirty Overflow
Deep Bed Liquid Pool
Having the best system possible:
• Producing higher rates • High quality rod• Less Maintenance • Increased roll life• Extended coolant life
Thank you