saving asset life - dga on ltcapic/uploads/forum/saving assets life.pdf · 3 dissolved gas analysis...
TRANSCRIPT
1
Saving Asset Life - DGA on LTC
2
DISSOLVED GAS ANALYSIS
■ Oil is the Life Blood of a Transformer
■ Like a blood sample, oil samples attempt to determine condition
3
DISSOLVED GAS ANALYSIS
■ Industry practice to use DGA for Transformer condition assessment
■ First IEEE Standard Formed in 1978 as C57.104
4
DISSOLVED GAS ANALYSIS
CAN THIS ASSESSMENT TOOL BE APPLIED FOR LOAD TAP
CHANGERS?
5
DGA on LTC
■ First introduction into Epcor in 2009 for trending
■ Discussion in the industry on adopting this as
standard for testing
■ IEEE standard was
created in 2010 –
C57.139
6
Garneau Substation Incident
■ Garneau Substation - 72kV 6
breaker ring bus with 3
transformers serving the
University Area
■ Garneau TX1 Details
■ 30/40 MVA Ferranti Packard
Transformer built in 1981
■ Load Tap Changer Type 25RT32
7
Garneau Incident and Investigation
DGA Test Results Received in August 2009
Gas PPM
H2 13,386
CH4 132,436
C2H6 70,740
C2H4 441,806
C2H2 19,570
TDCG 678,289
■ Using Themography LTC was confirmed warmer than main tank
■ Next Scheduled Maintenance due in 2010
8
Garneau TX1
9
Garneau TX1
10
Garneau TX1
11
Garneau TX1
12
Garneau TX1
13
Garneau TX1
14
Garneau Incident and Investigation
DGA Test Results Received 6 months Later
Gas PPM
H2 453
CH4 147
C2H6 156
C2H4 1273
C2H2 1092
TDCG 3161
■ Discussing with Siemens – service announcement April 2003 offering
reversing switch upgrade kit
■ Made repairs to TX1, TX2, TX3
15
Garneau Conclusions and Recap
■ Opening compartment confirmed indications of problems in tap
changer
■ Discussion with Vendor from incident led to installing Reversing
Switch upgrade kit
■ DGA results in 2010 and after confirmed successful repair
■ Originally scheduled for maintenance 2010 – unsure if tap changer
would have failed.
16
Thank you for your time
Any Questions?